Код: Выделить всё
# ls -alg /dev | grep ttyd
crw-rw-rw- 1 root nut 0, 47 26 фев 13:18 ttyd0
crw-rw-rw- 1 nut wheel 0, 48 26 фев 13:18 ttyd0.init
crw-rw-rw- 1 nut wheel 0, 49 26 фев 13:18 ttyd0.lock
Код: Выделить всё
#cat /usr/local/etc/nut/ups.conf
[Mustek]
driver = megatec
port = /dev/ttyd0
#cat /usr/local/etc/nut/upsd.conf
MAXAGE 15
LISTEN 127.0.0.1 3493
MAXCONN 1024
cat /usr/local/etc/nut/upsmon.conf
RUN_AS_USER nut
MONITOR Mustek@localhost 1 Mustek MussPass master
MINSUPPLIES 1
SHUTDOWNCMD "/sbin/shutdown -p +0"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
RBWARNTIME 43200
NOCOMMWARNTIME 300
FINALDELAY 5
# cat /usr/local/etc/nut/upsd.users
[Mustek]
password = MussPass
upsmon master
Код: Выделить всё
/usr/local/etc/rc.d/nut start
Network UPS Tools - UPS driver controller 2.4.1
Network UPS Tools - Megatec protocol driver 1.6 (2.4.1)
Can't uu_lock ttyd0: creat error: Permission denied
Driver failed to start (exit status=1)